|  | I can't find a Dec std 9 listing for AS255, but the
surge current should be below 70A max.
For VRC21:
AC power group A
Nominal voltage:     100-240 Volts, single phase
Voltage range:       88-256
Nominal frequency:   50-60 Hz
Frequency range:     47-63 Hz
Number of AC phases: 1
Input current:     Typical           Maximum
   Phase A:          1.5 Amps          2.4 Amps
   Phase B:          0.0 Amps          0.0 Amps
   Phase C:          0.0 Amps          0.0 Amps
   Neutral:          0.0 Amps          0.0 Amps
   Ground:           0.0 milliAmps     0.0 milliAmps
Power consumption:    90 Watts         150 Watts
Standby power consumption:              30 Watts
Apparent power (maximum):                0 Volt-Amperes
Inrush current:     70.0 Amps
Start-up current:   70.0 Amps
Start-up duration:   1.0 seconds
Power factor:  0.45
Crest factor:  0.00
AC power group B
Nominal voltage:     100-240 Volts, single phase
Voltage range:       88-256
Nominal frequency:   50-60 Hz
Frequency range:     47-63 Hz
Number of AC phases: 1
Input current:     Typical           Maximum
   Phase A:          1.0 Amps          1.3 Amps
   Phase B:          0.0 Amps          0.0 Amps
   Phase C:          0.0 Amps          0.0 Amps
   Neutral:          0.0 Amps          0.0 Amps
   Ground:           0.0 milliAmps     0.0 milliAmps
Power consumption:    90 Watts         150 Watts
Standby power consumption:              30 Watts
Apparent power (maximum):                0 Volt-Amperes
Inrush current:     60.0 Amps
Start-up current:   45.0 Amps
Start-up duration:   1.0 seconds
Power factor:  0.50
Crest factor:  0.00
 |